200’ is a long way for #6 copper. The barn is 200’ plus whatever is run in the wall to the panel. Without looking at a table I don’t think you can do it without #4 copper because of voltage drop.
For longer runs aluminum is half the price even though you have to upsize it a bit, and it’s twice as stiff so larger conduit is always better than smaller.