Electrical question

200’ is a long way for #6 copper. The barn is 200’ plus whatever is run in the wall to the panel. Without looking at a table I don’t think you can do it without #4 copper because of voltage drop.

For longer runs aluminum is half the price even though you have to upsize it a bit, and it’s twice as stiff so larger conduit is always better than smaller.
 
This is a pole barn for storage, and we just need lights and few outlets.
You may not need much at all:

I pieced my system together, but this is similar in size to what I've got going on at camp. In the winter without running a/c I don't run the generator and I've worked (lived) there for 10+ days just on the solar with the fridge running 24/7, everything on except a/c. I have all this setup on a "generator shed" the size of a doghouse about 80' away from the structures and feed it to the subpanel on the cabin with a 3500 watt generator extension cord and have another feed going to the bunkhouse subpanel as well.
 
I had asked what wire to run direct bury-what wire do you suggest? And to not further be confused, are you suggesting conduit or not?
If it were me my first pick would be running conduit sized for a 100A sub panel. That way you or anyone that follows are set for upgrading to whatever cable you want to run. If you were to ever put a proper sub panel out there I’d pull the appropriate sized aluminum cable. Far more cost effective than copper for longer runs.
 
If it were me, I'd run 2-2-2-4 to a 100 amp subpanel. That way you'll at least have some room to grow later if you decide you need more circuits.


 
#1/0-1/0-1/0-2 quadriplex URD aluminum wire. Just dig a trench a bury it. No need to run 200’ of conduit in my opinion. Even pvc is expensive these days. Knowing nothing about your current home service, I’d assume it is a 200a - which means sending a #1/0 aluminum wire out to a shop will probably give you enough room for future expansion without costing an arm/leg now.

Take your existing RV plug off the wall and put in a junction box. Make sure you have a black/red/white/(green or bare copper/aluminum) wires. Splice the old wires to the new wires and roll on.
 
#1/0-1/0-1/0-2 quadriplex URD aluminum wire. Just dig a trench a bury it. No need to run 200’ of conduit in my opinion. Even pvc is expensive these days. Knowing nothing about your current home service, I’d assume it is a 200a - which means sending a #1/0 aluminum wire out to a shop will probably give you enough room for future expansion without costing an arm/leg now.

Take your existing RV plug off the wall and put in a junction box. Make sure you have a black/red/white/(green or bare copper/aluminum) wires. Splice the old wires to the new wires and roll on.
Yes, 200 amp service, with a 50 amp RV service already outside on a post. Want to use that as power to feed the pole barn. I already have a finished shop, as mentioned lights and outlets is all I need. There won't be a down the line change, as this is storage. Shop vac, table saw, maybe a pancake compressor tops.

The lights several have recommended are LED high bays, around 200 watts each. Not sure if I need 6 or 10, going to test it out first.
 
If it were me my first pick would be running conduit sized for a 100A sub panel. That way you or anyone that follows are set for upgrading to whatever cable you want to run. If you were to ever put a proper sub panel out there I’d pull the appropriate sized aluminum cable. Far more cost effective than copper for longer runs.

How can I power a 100amp sub panel from a 50 amp rv service? I was told I won't even get a true 50 amps because of the distance and loss.

You have confused me again Bob!
 
Calculation is below.

Probably go one size up for added length of your run.

Also, for connecting to underground PVC, use 90 degree sweeps or you can buy non-metallic UALA. Which is like flexible conduit but rated to pull wire through.

If you were in Northern California then I could set you up. But any electrical supply house should be able to get you figured out.

The conduit size recommended is 3/4". I would go larger as it makes it easier to pull. Schedule 40 would work.
34f5945bdd087fad12c7bb2a24ac6074.jpg


Sent from my SM-S918U using Tapatalk
 
How can I power a 100amp sub panel from a 50 amp rv service? I was told I won't even get a true 50 amps because of the distance and loss.

You have confused me again Bob!

Is it just a pole outside that already has 50 amp right where you are running from? Or an exterior wall with an outlet you are drawing off of?


Might not be a concern now, but do something so its marketable in the future, its almost always money well spent.
 
Is it just a pole outside that already has 50 amp right where you are running from? Or an exterior wall with an outlet you are drawing off of?


Might not be a concern now, but do something so its marketable in the future, its almost always money well spent.
Yes it’s a post outside that has 50 amp RV service which I no longer need.

I don’t want to drill through foundation or tie into panel as this is readily available.
 
Yes it’s a post outside that has 50 amp RV service which I no longer need.

I don’t want to drill through foundation or tie into panel as this is readily available.

How much further would it be to get to the edge of the panel and run a dedicated line?

There's different places, something places you do what it takes to get by, some you do with plans to upgrade. An outdoor building on a decent property it would be hard for me not to spend the little more to make it easy to upgrade later, if not for you, for the potential resale value, or a home inspector coming through and killing a sale going WTF.

If only lights, I'd probably look more and more at solar, or wire the building and picking up a cheap generator. Those are always handy.
 