Electrical question

@Team4LongGun,
Maybe this is all settled now, but I’ll chime in. In conduit is best and future-proof, but it’s not a requirement. With what you want to do, just get AL direct bury wire and send it. Looks like the electricians here have figured wire size and voltage drop.

If you need an equipment grounding conductor, meaning 4-wire cable instead of just 3-wire cable, your best option would be to go to an electrical supply house and get 2/0 MHF cable, also known as 2/0 mobile home feeder wire. It’s rated for direct burial.
 
Because some day down the road you start spending more time in your shop and decide that you want something more than lights.
Great looking ahead, but I have addressed this several times, and it has been missed.

This is ONLY ever to be storage. I have a finished shop. This is a pole barn and only needs lights.
The good idea fairy is alive and well! 😄

Several of you have helped me dial this in, thank you.
 
  • Like
Reactions: BLJ
Because some day down the road you start spending more time in your shop and decide that you want something more than lights.
I understand, but when he has been specific, multiple times, about only needing lights and some outlets, and only has a 50A supply, I’m just gonna tell him how to do that properly.

I’m not jumping on your case, just trying to help the OP.
 
  • Like
Reactions: BLJ

There's no need to overcomplicate the situation. I would use a conduit as risers coming in and out of the ground. But you can just leave the ends in the ground and direct bury the rest.
With that much distance expect some de-rating. I wouldn't try to push a full 50 amps. But otherwise that is plenty for just some lights and plugs.
 

If would recommend throwing one of these in that trench too while it's open. If you want internet out in the barn.

But after thinking about it. I would honestly put a 40 amp main breaker in your sub-panel just to be safe because of the distance. Even though it's being fed by a 50.

But for reference I put 40 amps in my garage and have a table sander, drill press, band saw, commercial freezer ect... you will still have plenty of juice.
 

If would recommend throwing one of these in that trench too while it's open. If you want internet out in the barn.

But after thinking about it. I would honestly put a 40 amp main breaker in your sub-panel just to be safe because of the distance. Even though it's being fed by a 50.

But for reference I put 40 amps in my garage and have a table sander, drill press, band saw, commercial freezer ect... you will still have plenty of juice.
I will do that ethernet cable, great idea.

Good to know your running those things on 40 amps, that is plenty for what we need.
 
Be careful listening to some of the “internet electricians”. Some have given spot on advice, some not so much.

Here is the answer to your wire size. This is for copper conductors. Aluminum will need a larger wire.
IMG_4519.png

You will need (3) #4 and (1) #10 ground wire.

I personally would never direct bury wire even if it’s rated for such. It will fail sooner than later and you will be replacing it.

You can technically use a 1” sch40 PVC conduit but I would upsize to 1-1/4 or 1-1/2. You never know what your future needs may be.

Hope this helps answer your question.

What are you planning to do at the RV receptacle? If you have no plans to use it, I would just remove it and replace it with a nema 3R junction box and wire in direct.
 