When you only have a 50A supply, what would be the point in over sizing wire?Conduit, and over size the wire for what you think you will ever need.
Because some day down the road you start spending more time in your shop and decide that you want something more than lights.When you only have a 50A supply, what would be the point in over sizing wire?
Great looking ahead, but I have addressed this several times, and it has been missed.Because some day down the road you start spending more time in your shop and decide that you want something more than lights.
I understand, but when he has been specific, multiple times, about only needing lights and some outlets, and only has a 50A supply, I’m just gonna tell him how to do that properly.Because some day down the road you start spending more time in your shop and decide that you want something more than lights.
I will do that ethernet cable, great idea.![]()
Cat6 Direct Burial Ethernet Cable|Shielded
Shielded Cat6 direct burial ethernet cable for outdoor use. 10Gbps speeds, 550MHz, pure solid copper, waterproof, UV resistant, 500ft/1000ft bulk reel.www.truecable.com
If would recommend throwing one of these in that trench too while it's open. If you want internet out in the barn.
But after thinking about it. I would honestly put a 40 amp main breaker in your sub-panel just to be safe because of the distance. Even though it's being fed by a 50.
But for reference I put 40 amps in my garage and have a table sander, drill press, band saw, commercial freezer ect... you will still have plenty of juice.
When I worked a service van one of the most common calls we fielded was tripped breakers that wouldn’t reset. Probably 80% of the time it was direct bury cable that had failed. Most of the time it was insulation breakdown causing a direct fault, sometimes it would be wet soil causing faults. Sometimes it would be rocks or something else that compromised the insulation. I’ve seen failures as soon as 5 years after installation and I’ve seen some that lasted 25 years.Everyone poo pooing on DB, how quickly do you think it fails? There are literally hundreds of thousands of houses that had DB wire services installed in the 60's-90's. To this day, many of them are still working. Many have faulted, but for this guy's needs and wants, it seems just fine. Extra care when installing it and good non rocky shading is key. Also, seems like minimal load will be applied to said wire in the OP's case. Obviously not the best way, but plenty functional and at a fraction of the price vs. conduit install.